Power for OSSD safety sensor at Safeguard input

Well. To reply to the rest of your topic: I don’t know why ts1 said you shouldn’t use the 24V of SI. As you said yourself, the 24V terminals are the same everywhere in the controller. :slight_smile:

What happens when you connect the device to the safeguard inputs? It should work.
Have you remembered to remove the Reset Safeguard inputs from CI0 and CI1 in Installation → Safety → IO? If this is not removed, the robot will not reset safeguard without a reset signal on CI0 and CI1.