Hello,
I am trying to communicate the UR robot with an Omron NJ series PLC using the UR robot as the modbus client.
I can read values from the holding registers and coils of the PLC but I can not send any registers or coils to it.
I followed the steps in this article: Modbus TCP Client Setup - 16363
The article is talking about register IDs. I couldn’t find the register IDs of the PLC I am using.
Normally, the PLC I use does not have modbus feature but I am using a modbus library which was developed using socket communication feature of the PLC and the datasheet of the library doesn’t include a register table like the one in this article.
I typed “0” in the register ID textfield when I was trying to read from the PLC and it worked.
But it didn’t work when I typed “0” or “30001” when I was trying to write to the holding register of the PLC.
I tried my own URCAP using this command to add a modbus signal: modbus_add_signal(IP, slave_number, signal_address, signal_type, signal_name, sequential_mode=False) Again, I was successful at reading the values from the PLC but couldn’t write to it.
Also, I can write to the holding registers of the PLC using C# code that I wrote via my PC.
In the C# code, I specify the registers like from the register 0 to 20. Then it writes the data I sent to all those register.
What should the register ID be? I reckon the signal address and the register ID are the same thing here? If not what should the signal adress be as well?
Thank you,
MB
The article states "For most devices under Modbus TCP the slave ID is not used and if that is the
case then it is set to 255" So I will suggest you set it to 255.
Ebbe
Hello,
I had already set the slave ID (slave number) to 255 as it was instructed in the urscript manual.
I am wondering what the signal address should be?
modbus_add_signal(IP, slave_number = 255, signal_address, signal_type, signal_name, sequential_mode=False)
And also are the address (marked below) and the signal address the same thing?
Thank you,
MB
The addresses you have marked in Polyscope, is what Polyscope uses for the signal_address in URScript. It is the register on you PLC that you need to specify here. A nice approach is to connect to local host on IP address “127.0.0.1” and add a Register Output signal with address 1. Then you will see that it maps to the outputs of the robot and you can modify them by writing a bit pattern in the value field.
Ebbe
Hello,
Thanks for the help Ebbe,
MB